Hi all,
Zurn best practices says to add 1/8" per foot of pex for expansion. They say to either loop or off-set 12" in bay. Is this applicable to potable hot and cold, and heating applications? |
|||
|
|
|
most pex will expand 1.1" per 10 degree rise per 100 feet of length. so if you install on a 60 degree day and you're running 150 degree water through it, that's a 90 rise, or 9.9" per hundred feet, or about 1/10 of an inch per foot.
so 1/8" per foot is definitely worst case. and it's not particularly applicable in potable applications, though if you install on a 90 degree day and you run 50 degree water through it, you might have issues on long runs.. ------------------------------ -=Northeast Radiant Technology, LLC=- Radiant Design, supply and consultation services. www.NRTradiant.com |
|||
|
I'll throw in a little tidbit here. When I installed my wood-fired, outdoor boiler years ago, I missed a small part of the instructions that said to leave extra pex and hook the underground pipe up above ground first and run the system through a heating/cooling cycle. Then cut the pex to length and bury it. The reason for doing this is that the pex initially expands upon heating and shrinks a LOT upon cooling. After the first cycle, the pipe will expand and contract - probably by Rob's formula. But that first cooling cycle shrinks the tubing and never returns it. I lost probably a foot of pex in 50 or 60 feet. Shoulda read the instructions a bit more carefully.
|
||||
|