5 circuits in a single zone all using 1/2" pex. What size pex should I use to feed the manifolds? Seems like 1" would be right for 4 circuits. Does the feed water velocity have to match that in the circuits (for moving air bubbles, noise etc)? Thanks
 
Posts: 28 | Location: United States | Registered: 05 February 2009Reply With QuoteEdit or Delete MessageReport This Post
Picture of NRT.Rob
Posted Hide Post
it could be anything up to and including 1", depending on your flow rates, distances, loop frictional losses and pump selection.

velocity does not need to match.


------------------------------
-=Northeast Radiant Technology, LLC=-
Radiant Design, supply and consultation services.
www.NRTradiant.com
 
Posts: 2249 | Location: Gardiner, ME | Registered: 09 March 2005Reply With QuoteEdit or Delete MessageReport This Post